When determining the correct conductor for terminations do you have to derate the ampacity because of a higher ambient temperature? For example I have a 69 amp load, I will be using 90C wire and my lowest termination is 60C. My ambient temperature is 40C. Following the rules for sizing my wire for the termination I come up with #2 wire if I don't derate for temperature. 69 times 1.25.
If I do derate for temperature I come up with #1.
(69 times 1.25)/0.91
What wire size should I use?
Does the change to 110.14 (C) (1) in 2002 make a difference? It tells me to use table 310.16 so I assume I have to derate the terminal for temperatures above 30C or does the derating only affect the conductor?