I have some single-phase 24VDC power supplies in an industrial control cabinet with a 208VAC wye supply.
The power supplies are rated for universal input, from 100 to 240VAC or something like that. The manufacturer stated over the phone and in an email that they can be connected in this case to either 120V (L-N) or 208V (L-L). One of the manuals specifically calls out 208VAC as a supply voltage option. I want to connect them L-L for current draw reasons.
The issue I'm having is that because the supply terminals are marked L and N on the device itself, the reviewer for this design is insisting that they must be connected L-N, despite what the manufacturer says.
Is there anything in the NEC, NFPA 79, or UL 508A that covers something like this?
The power supplies are rated for universal input, from 100 to 240VAC or something like that. The manufacturer stated over the phone and in an email that they can be connected in this case to either 120V (L-N) or 208V (L-L). One of the manuals specifically calls out 208VAC as a supply voltage option. I want to connect them L-L for current draw reasons.
The issue I'm having is that because the supply terminals are marked L and N on the device itself, the reviewer for this design is insisting that they must be connected L-N, despite what the manufacturer says.
Is there anything in the NEC, NFPA 79, or UL 508A that covers something like this?