TB's in non-explosion proof enclosures in Class 1 Div 1 and 2 areas

Status
Not open for further replies.

Lucas991

Member
Location
Houston
Occupation
Electrical Engineer
I have a project where I will locate a NEMA 4X enclosure inside a Class 1 Division 2 area. Inside this enclosure I will house a Class 1 Div 2 (potted) heater,
a Class 1 Div 1 explosion-proof instrument (with seal for incoming cable), and a Class 1 Div 2 rated (potted) temperature switch for controlling the heater.
The only other electrical component I have is a terminal block. I'm under the impression that a terminal block (whether DIN rail mounted or
panel mounted) is a non-arcing / non-sparking device which also does not generate heat under normal operating conditions therefore the
terminal block can be used inside this non-explosion rated enclosure.

I would also like to know if the same rules apply for a Class 1 Div 1 area if all my other electrical parts were rated for Class 1 Div 1 (and sealed where necessary) and only the TB was unrated.

All loads are rated at 120VAC except for the 24VDC instrument.

Thank you,

Lucas
 
Last edited:

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
If you were only dealing with Division 2, you would be fine. However see Section 501.10(A)(3) for Division 1 applications.
 