Tap off sub panel

Location
Nj
Bare with me it's been a long time. Where I work there's a 225 amp main lug subpanel fed by a main distribution. 225 amp breaker.
They want a subpanel somewhere near the facility so this panel would be nice to tap off of. Are you allowed to get power from a panel with out the main breaker in the panel?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Sure but the tap rules would apply if the conductors to the new panel are smaller than the OCPD ahead of the existing panel.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
But if you actually mean the feeder on a breaker in the sub-panel, no problem at all.
I meant that the tap rules would apply because he said "tap" and made no mention of adding a breaker but who knows exactly what the OP means by "tap".
 

NoahsArc

Senior Member
Location
Illinois
Occupation
Residential EC
Per 215.3, 240 pt I generally applies. Pt II is by and large irrelevant other than basics that are already covered by the current subpanel.
The tap conductors downstream (in this instance not "tap" tap conductors) are protected by the CB at the point of the tap.
 