t12 electronic ballast

Status
Not open for further replies.

fireryan

Senior Member
Location
Minnesota
When changing out a t12 ballast to a t12 electronic ballast are you really seeing any energy savings? Isnt most of the energy savings coming into play when you are switching out to a t8 tube?
 

bob

Senior Member
Location
Alabama
The ballast itself consumes wattage. Check the old ballast for wattage consumed. The electronic ballast consumption is near zero. You would be ahead to change the bulbs also. I am going on memory but 4 bulb t12 40w with 2 ballast consumes about 200 watts. 4 t8 consuption is about 112 watts.
 

tshea

Senior Member
Location
Wisconsin
GE Ballasts, 2 lamp, 120 volt, ballast factor .87:
2 lamp F34T12 magnetic ballast: system watts 93*
2 lamp F34T12 electronic ballast: system watts 63
2 lamp F32T8 electronic ballast: system watts 49

Source: GE Lamp & Ballast Catalog

*Note: no longer made. Also an educated guess based on current of .77 A * 120V = 92.4 watts.
 