Surge Protection

Status
Not open for further replies.

schoome

Member
I am installing some surge protection in a residential loadcenter and have a couple of questions. I was told to wrap the neutral wire around the two power wires that feed the surge suppressor from the circuit breaker mounted to the buss, why.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Re: Surge Protection

Told by whom? This sounds odd to me. Is it in the manufacturer's instructions?
 

dereckbc

Moderator
Staff member
Location
Plano, TX
Re: Surge Protection

Proper installation is to twist, not wrap, all the conductors to the TVSS together to closely couple them magnetically together. This will minimize (cancell) the voltage drop incurred during a TVSS event. In addition the conductors should be no longer than 6-inches from the device to point of connection to retain the UL-1440 SVR.
 

pierre

Senior Member
Re: Surge Protection

Derek
Do you mean to twist the conductors together like 'twisted' pair wiring?

If so, since the ungrounded conductors are terminated at a different location than the grounded conductors, would it make any difference if one was to twist them for even just a short distance?
 

dereckbc

Moderator
Staff member
Location
Plano, TX
Re: Surge Protection

Originally posted by pierre:
Derek
Do you mean to twist the conductors together like 'twisted' pair wiring?
YES! That is why it is preferable to use a panel with built in TVSS rather than add-ons. With an add-on unit (parallel), it is almost impossible?to install per UL-1449 and ANSI C61.42 recommendations.
 