I have an application where a 208/120V rated SPD is being used on a 400/230V (European) application. Reading NEC 285.3 (3) it states "Where the rating of the SPD is less than the maximum continuous phase-to-ground power frequency voltage available at the point of application". Talking to various vendors, some have stated that 208/120V rating would preclude use at the higher voltage application (120V vs. 230V), but others have stated that the MCOV (maximum continuous operating voltage) rating may allow these SPDs to be used at these higher voltages. In my case, the device has an MCOV of 550/275V.
Can someone confirm if the MCOV is means to allow a lesser system voltage rated SPD to be used if the nominal operating voltage falls within the MCOV range, or is this to account for fluctuations in the system voltage? Does an SPD 'rating' per the NEC refer solely to its nominal system voltage rating, or does it also account for the MCOV as part of its 'rating?
Thanks.
Can someone confirm if the MCOV is means to allow a lesser system voltage rated SPD to be used if the nominal operating voltage falls within the MCOV range, or is this to account for fluctuations in the system voltage? Does an SPD 'rating' per the NEC refer solely to its nominal system voltage rating, or does it also account for the MCOV as part of its 'rating?