I have a warehouse that put in multiple stand up water coolers with water supply lines attached, they plugged them into a 110 outlet, do they need to change the normal outlet to a GFCI outlet?
 

Paul Pugliese

Member
Location
15116
Occupation
Safety Professional
On my safety walk I found a Breaker panel that the door latch was broken is the a code that covers the door of the breaker panel door must be closed and latched?
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
On my safety walk I found a Breaker panel that the door latch was broken is the a code that covers the door of the breaker panel door must be closed and latched?
The NEC is not a maintenance code. Depending on your jurisdiction, it is likely covered under the fire code.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
On my safety walk I found a Breaker panel that the door latch was broken is the a code that covers the door of the breaker panel door must be closed and latched?
Breaker panels are not even required to have doors so I don't see any issue.
 