splicing to different size wires with proper amperage rating

Status
Not open for further replies.

JH13

Member
Location
New Jersey
Occupation
facilities electrician
i am doing calculations for wire size needed after derating for amount of conductors in the conduit. my question is: can i down size my wire once i hit the gutter and all circuits are split up into different runs? or do i need to continue the same gauge wire to all of the equipment even though no derating is needed when they exit the gutter?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
As Dave stated in the wireway once you exceed 30 CCC's you'll need to derate. If you don't have more than 30 CCC's at any cross section then you can use smaller conductors without any derating being applied.
 