ruxton.stanislaw
Senior Member
- Location
- Arkansas
- Occupation
- Laboratory Engineer
Is the nominal voltage field programmable on the SolarEdge SE100K-US? We are looking for a similar set of inverters, with a target voltage of ~ 440Y/254V.
Is the nominal voltage field programmable on the SolarEdge SE100K-US? We are looking for a similar set of inverters, with a target voltage of ~ 440Y/254V.
Inverter AC voltage is not programmable; the inverter synchs to the line voltage as long as it is within its voltage range. That range is expandable on some inverters, but in any case 440V will be very close to the lower bound if it is in the range at all, so even if it is it won't take much of a dip in line voltage to shut the inverter(s) down. Have you considered using a buck-boost transformer to boost the line voltage to 480V?Is the nominal voltage field programmable on the SolarEdge SE100K-US? We are looking for a similar set of inverters, with a target voltage of ~ 440Y/254V.
On some models of inverters, you can program the AC voltage range to non-US standard settings and allow it to operate on foreign grids. You will inevitably take a hit to your maximum power, since maximum current can't be changed. This means a 100 kW inverter built for a 277/480V grid, would effectively act as an 91 kW inverter on a 254/440V grid.Inverter AC voltage is not programmable; the inverter synchs to the line voltage as long as it is within its voltage range. That range is expandable on some inverters, but in any case 440V will be very close to the lower bound if it is in the range at all, so even if it is it won't take much of a dip in line voltage to shut the inverter(s) down. Have you considered using a buck-boost transformer to boost the line voltage to 480V?
Inverter AC voltage is not programmable; the inverter synchs to the line voltage as long as it is within its voltage range. That range is expandable on some inverters, but in any case 440V will be very close to the lower bound if it is in the range at all, so even if it is it won't take much of a dip in line voltage to shut the inverter(s) down. Have you considered using a buck-boost transformer to boost the line voltage to 480V?
The current being the limiting factor makes sense; we are OK with that compromise. This is mostly for 240 and 400 V single phase (VFDs or hot water tanks) rated equipment. With the voltage tolerance range of the equipment and voltage drop in mind, I arrived at the 254 V target, choosing the upper end of the range for efficiency.This means a 100 kW inverter built for a 277/480V grid, would effectively act as an 91 kW inverter on a 254/440V grid.
Off grid is a different ball of wax. What are you using for storage? How are you furnishing line voltage to the inverters?Thanks guys. This is for off-grid use in a rural area, sorry I did not make that clear. There will be an ATS after the inverter system, for a generator.
I need an inverter that can operate islanded and lead the system with its own frequency.Off grid is a different ball of wax. What are you using for storage? How are you furnishing line voltage to the inverters?
The SolarEdge SE100K-US will not do that. Off grid PV operation generally requires storage.I need an inverter that can operate islanded and lead the system with its own frequency.
Thank you for confirming this. My other consideration is for two SOL-ARK 60K-3P-480V inverters (https://www.sol-ark.com/sol-ark-60k-3p-480v-n/) in parallel. I have a request out to the Sol-ark engineering team to confirm which off-grid grid level configuration options are available.The SolarEdge SE100K-US will not do that.
Good luck with that, and let us know what they say.Thank you for confirming this. My other consideration is for two SOL-ARK 60K-3P-480V inverters (https://www.sol-ark.com/sol-ark-60k-3p-480v-n/) in parallel. I have a request out to the Sol-ark engineering team to confirm which off-grid grid level configuration options are available.
View attachment 2569893
Pursue that. Don't bother with SolarEdge, especially for this. Multiple reasons.Thank you for confirming this. My other consideration is for two SOL-ARK 60K-3P-480V inverters (https://www.sol-ark.com/sol-ark-60k-3p-480v-n/) in parallel. I have a request out to the Sol-ark engineering team to confirm which off-grid grid level configuration options are available.
View attachment 2569893
I have designed many commercial PV systems with SolarEdge inverters and they are all doing just fine.Pursue that. Don't bother with SolarEdge, especially for this. Multiple reasons.
And I have installed many residential Solaredge inverters and they have not all done just fine. But I said that mainly because this is an off-grid application. Sol-Ark is built around off-grid as a company in a way that SE is completely not.I have designed many commercial PV systems with SolarEdge inverters and they are all doing just fine.
What sorts of problems did you encounter?And I have installed many residential Solaredge inverters and they have not all done just fine.
Lots of failed inverters and optimizers. And pretty terrible support dealing with it.What sorts of problems did you encounter?