I've got a customer with two main breaker meter mains that wants to have solar installed. Can the breaker for the solar be located in a sub-panel or does it have to be located in the main service? Thanks
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
I've got a customer with two main breaker meter mains that wants to have solar installed. Can the breaker for the solar be located in a sub-panel or does it have to be located in the main service? Thanks
You may install PV in a subpanel if your AHJ allows it, but 705.12(B)(3) must be satisfied for every busbar between the interconnection and the service, including those in the meter main.
 