Indiana Administrative Code Page 35
675 IAC 14-4.2-31 Section R317; smoke alarm
Authority: IC 22-13-2-2; IC 22-13-2-13; IC 22-11-18
Affected: IC 22-12; IC 22-13; IC 22-14; IC 22-15; IC 36-7
Sec. 31. Delete the text of SECTION R317 and substitute to read as follows:
R317.1 Labeling. Each smoke alarm shall be listed.
R317.2 Required smoke alarm locations. At least one (1) smoke alarm shall be installed in each of the following locations:
(a) In the living area remote from the kitchen and cooking appliances. Smoke alarms located within twenty (20) feet (six and
one-tenth (6.1) meters) horizontally of a cooking appliance must incorporate a temporary silencing feature or be photoelectric
type.
(b) In each room designed for sleeping.
(c) On the ceiling of the upper level near the top or above each stairway, other than a basement stairway, in any multistory
dwelling. The alarm shall be located so that smoke rising in the stairway cannot be prevented from reaching the alarm by an
intervening door or obstruction.
(d) On the basement ceiling near the stairway.
R317.2.1 Alterations and additions. When interior alterations or additions requiring a permit occur, or when one (1) or more sleeping
rooms are added or created in existing dwellings, the individual dwelling unit shall be provided with smoke alarms located as
required for new dwellings; the smoke alarms shall be interconnected and hard wired.
EXCEPTIONS: 1. Smoke alarms in existing areas shall not be required to meet the requirements of R317.5 where the
alterations do not result in the removal of the interior wall or ceiling finishes exposing the structure unless there is an attic,
crawlspace, or basement available which could provide access for hard wiring and interconnection without the removal of
interior finishes.
2. Repairs are exempt from the requirements of the section.
R317.3 Prohibited smoke alarm locations. A smoke alarm required under this section shall not be placed:
1. within three (3) feet (nine hundred fourteen (914) millimeters) horizontally from any grille moving conditioned air within
the living space; or
2. in any location or environment that is prohibited by the terms of the listing.
R317.4 Mounting requirements. Smoke alarms required by SECTION R317.2 shall be mounted in accordance with their listing,
instructions, and the requirements of this section.
R317.4.1 Flat Ceilings. In rooms with flat, peaked sloping or single slope ceilings with a slope of less than 1.5/12, smoke alarms
shall be mounted either:
1. on the ceiling at least four (4) inches (one hundred two (102) millimeters) from each wall; or
2. on a wall with the top of the alarm not less than four (4) inches (one hundred two (102) millimeters) below the ceiling and
not farther from the ceiling than twelve (12) inches (three hundred five (305) millimeters) or the distance from the ceiling
specified in the smoke alarm manufacturer’s listing and instructions, whichever is less.
R317.4.2 Peaked Sloping Ceilings. In rooms with peaked sloping ceilings with a slope of 1.5/12 or greater, smoke alarms shall be:
1. mounted on the ceiling or wall within three (3) feet (nine hundred fourteen (914) millimeters), measured horizontally, from
ONE AND TWO FAMILY DWELLING CODE
the peak of the ceiling;
2. at least four (4) inches (one hundred two (102) millimeters), measured vertically, below the peak of the ceiling; and
3. at least four (4) inches (one hundred two (102) millimeters) from any projecting structural element.
R317.4.3 Single Slope Ceilings. In rooms with single slope ceilings with a slope of 1.5/12 or greater, smoke alarms shall be:
1. mounted on the ceiling or wall within three (3) feet (nine hundred fourteen (914) millimeters), measured horizontally, of
the high point of the ceiling; and
2. not closer than four (4) inches (one hundred two (102) millimeters) from any adjoining wall surfaces or any projecting
structural element.