Sleeves

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Sure Infinity would be aware of this situation :), IUn annew construction job and these conduits and cables going up 3-4 floors would you HAVE to put sleeves in of would you get your conduits in before theslab pour? Which is more likely? Thanks

1715944272387.png
 

Rick 0920

Senior Member
Location
Jacksonville, FL
Occupation
Electrical Instructor
There are several ways to accomplish this. Personally, if I have as much as shown in the graph above, I would create a blockout before the slab pour and then firecaulk or fill with other approved means after all my conduits and cables were installed. Core drilling is also another option. It doesnt take as long as some people think to set up and core holes. Precise cutting after the pour can make installations easier and with fewer bends. Also take into account if your vertical runs are straight, you will need strain reliefs for your conductors and cables.
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
There are several ways to accomplish this. Personally, if I have as much as shown in the graph above, I would create a blockout before the slab pour and then firecaulk or fill with other approved means after all my conduits and cables were installed. Core drilling is also another option. It doesnt take as long as some people think to set up and core holes. Precise cutting after the pour can make installations easier and with fewer bends. Also take into account if your vertical runs are straight, you will need strain reliefs for your conductors and cables.
Thanks. Why not just get the strut framing shown and conduits in before the pour?
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
There are several ways to accomplish this. Personally, if I have as much as shown in the graph above, I would create a blockout before the slab pour and then firecaulk or fill with other approved means after all my conduits and cables were installed. Core drilling is also another option. It doesnt take as long as some people think to set up and core holes. Precise cutting after the pour can make installations easier and with fewer bends. Also take into account if your vertical runs are straight, you will need strain reliefs for your conductors and cables.
100% I would do this. Block out the floor for this many conduits. Then I would contact your preferred firestopping manufacturer and find the best sealing solution. My first instinct is Fire Blocks such as what Hilti has. Much less work than sleeves for every item. Check out Fire Block Hilti on Google, or better yet call their 800 number and talk to a specialist.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If you can run the conduits before the pour. That eliminates all the costs associated with firestopping.
 

Rick 0920

Senior Member
Location
Jacksonville, FL
Occupation
Electrical Instructor
If you can run the conduits before the pour. That eliminates all the costs associated with firestopping.
I still think a blockout would be best in this instance. Minimal sealing would be needed if you just used a hole saw on the floor decking, then you can just mix up some concrete and fill the blockout after sealing around the holes.
 