Slash rated breaker

Status
Not open for further replies.

Lucas Organ

Member
Location
NL CANADA
Occupation
Industrial Electrician
Guys I have a slash rated breaker 60/75 degrees. Which degree column would I use out of table 2 CEC to size my wire?

Thanks looking forward to all the input
 

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
I’m probably sticking my nose where it doesn’t belong ( I don’t use CEC) but probably also depends on type of cable you are using, if it is a cable you are using, and also the equipment the conductors are terminating and what degree it’s rated for.
 

Eddy_Current

Member
Location
Canada
Guys I have a slash rated breaker 60/75 degrees. Which degree column would I use out of table 2 CEC to size my wire?

Thanks looking forward to all the input
Like I told you in the other thread, there is nothing in the CEC on this. Here is the bulletin from Ontario that allows us to use the higher rating.
BD588233-CA84-42DF-AE37-FA539E6D06C1.png
 
Status
Not open for further replies.
Top