HoosierSparky
Senior Plans Examiner, MEP
- Location
- Scottsdale AZ
- Occupation
- Senior Plans Examiner
I have a storage battery that per it's specs has an output of 32A and required circuit breaker protection at 30a. Applicant is calling out #10. Do I size the feeder at 125% of output? Also there is a temp derate to 0.84 for our ambient. I'm thinking #8.