I seen a post relating to this I thought, but I can’t find it. So I’m going to ask anyways.
How does one properly size bonding jumpers, say from myer hubs to the rest of the panel case. In my company I’ve always just seen #10 or #12 used, probably because it’s small easy to work with and convenient.
But how does one properly size the conducter to be used say if you had a distribution panel with, #2 feeder and other smaller branch circuits.
If I am correct I know that if Under 250volts you don’t have to worry about it, but most the gas company’s we work for spec out for everything to be continues and bonded regardless of voltage.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Please note 250.102(C) is for service and supply side bonding jumpers and 250.122 is for feeder and branch circuit bonding jumpers.
If you have multiple hubs and are bonding on the load side of overcurrent devoces you can use one jumper sized to the largest device. See 250.102(D)
 

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
I am not sure what you have there. Are these service raceways or just feeders and branch circuit raceways?
Just feeders and branch.

I’ll build a senerio . 100amp distribution panel with 1.5in rigid conduit entering with #2 feeders. Than 3, 1” conduits leaving with 20amp branch circuits. If I were to daisy chain all the hubs I’d only have to take the larger bonding jumper to the 1.5” myerhub and after that reduce down to what I would need for the 20 amp branch circuits right?
 
Last edited:

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
So why are you bonding them. I assume you are using metal conduit??? Do you have an equipment grounding conductor run in the conduits also?

As Gus stated for feeders and branch circuits you would use T 250.122
 

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
Yes we have rigid conduit, and EGC but the gas company specs out for grounding type myer hubs to be bonded. However I’ve never known there to be a specific size conducter for them. I know what we’re doing is basically for looks and to please the customer.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I would use T 250.122 for bonding the raceways based on the largest conductor in any of the raceways - that is assuming you are bonding them as a continuous run.
 

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
For example in this photo it is not yet done. The largest EGC in the box is a number 8. So if I was I daisy change all the hubs would I have to use #8 on them all, even the conduit hubs with a smaller EGC, or just to that specific conduit it comes from?
 

Attachments

  • 40458C7B-3478-43EE-BA64-639F0EC9F0FC.jpeg
    40458C7B-3478-43EE-BA64-639F0EC9F0FC.jpeg
    90.6 KB · Views: 29

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
Stole this pic off the web. Obviously I don’t know Conductor sizes but can tell the bonding conductor is significantly smaller.
 

Attachments

  • 8BCFB564-2564-4296-B061-A61462898F47.jpeg
    8BCFB564-2564-4296-B061-A61462898F47.jpeg
    265.1 KB · Views: 19

kwired

Electron manager
Location
NE Nebraska
Stole this pic off the web. Obviously I don’t know Conductor sizes but can tell the bonding conductor is significantly smaller.
Seems to be pretty good chance that jumper is not large enough.

If those raceways contain parallel sets, even more likely.

Add: 99.99% of the time would need to be size of the green pulled in the raceway.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Stole this pic off the web. Obviously I don’t know Conductor sizes but can tell the bonding conductor is significantly smaller.
I agree with Kwired that bonding jumper is not sized properly. At the minimum it should be the same size as the EGC.
 

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
Seems to be pretty good chance that jumper is not large enough.

If those raceways contain parallel sets, even more likely.

Add: 99.99% of the time would need to be size of the green pulled in the raceway.
That’s what I was under the impression of.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The green bonding conductor in the pic doesn't even look as large as the egc in the conduit. Anyway the OP is not talking parallel runs so the bond can be sized based on T250.122 based on 250.102 (D) as Gus stated
 

Carultch

Senior Member
Location
Massachusetts
Please note 250.102(C) is for service and supply side bonding jumpers and 250.122 is for feeder and branch circuit bonding jumpers.
If you have multiple hubs and are bonding on the load side of overcurrent devoces you can use one jumper sized to the largest device. See 250.102(D)

What happens when the size specified in either 250.102(C) or 250.122, which ever is applicable, is too large to fit in the bonding bushing lug?

I could see this as a likely situation, when you have a large quantity of parallel sets.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The green bonding conductor in the pic doesn't even look as large as the egc in the conduit. Anyway the OP is not talking parallel runs so the bond can be sized based on T250.122 based on 250.102 (D) as Gus stated
Dennis, why would parallel conductors change anything? Wouldn't the EGC in each raceway need to be "full size" anyway?

What happens when the size specified in either 250.102(C) or 250.122, which ever is applicable, is too large to fit in the bonding bushing lug?

I could see this as a likely situation, when you have a large quantity of parallel sets.
You change the lug, done all of the time because they never seem to be large enough. :)
 