I'm under the 2002 code.
I'm trying to properly size the bonding jumpers for the service entrance conduits (2 ea. parallel 4" RMC.
The service is 480/277V 3ph, 4 wire, feeding an 800A fusible service disconnect switch.
All wire is Cu, THHN.
The service is 2 ea. parallel sets of 4 ea #600 Kcmil. The drawings also call for a #1/0 Cu. ground wire in each service conduit (in addition to the neutral), to be run out to the utility pad mt. transformer.
Why is the 1/0 ground being run within each service conduit? How did they get 1/0 as the correct size?
For the service conduit bonding jumpers, I think that 250.102(C) would apply, right? If so, then...
600+600 = 1200 Kcmil would be the largest service phase conductor? So 1200 x 12.5% = 150 Kcmil, minimum size, right?
So the jumper to each 4" service conduit would need to be #3/0 cu (=167 Kcmil), right?
If #3/0 is correct, can a single 3/0 be run from the ground bus to the first 4" conduit, then looped to the second 4"? Or do you have to run an individual 3/0 from the ground bus to each 4" conduit? Grounding bushings will be used on the conduit ends.
What size does the main bonding jumper (from neutral to ground bus) have to be? The GEC is shown as 3/0 Cu ran from the ground bus to the building steel and to the UG water pipe. I think the main bonding jumper should be 3/0, but I'm not sure where to find that in the code?
Thanks!
I'm trying to properly size the bonding jumpers for the service entrance conduits (2 ea. parallel 4" RMC.
The service is 480/277V 3ph, 4 wire, feeding an 800A fusible service disconnect switch.
All wire is Cu, THHN.
The service is 2 ea. parallel sets of 4 ea #600 Kcmil. The drawings also call for a #1/0 Cu. ground wire in each service conduit (in addition to the neutral), to be run out to the utility pad mt. transformer.
Why is the 1/0 ground being run within each service conduit? How did they get 1/0 as the correct size?
For the service conduit bonding jumpers, I think that 250.102(C) would apply, right? If so, then...
600+600 = 1200 Kcmil would be the largest service phase conductor? So 1200 x 12.5% = 150 Kcmil, minimum size, right?
So the jumper to each 4" service conduit would need to be #3/0 cu (=167 Kcmil), right?
If #3/0 is correct, can a single 3/0 be run from the ground bus to the first 4" conduit, then looped to the second 4"? Or do you have to run an individual 3/0 from the ground bus to each 4" conduit? Grounding bushings will be used on the conduit ends.
What size does the main bonding jumper (from neutral to ground bus) have to be? The GEC is shown as 3/0 Cu ran from the ground bus to the building steel and to the UG water pipe. I think the main bonding jumper should be 3/0, but I'm not sure where to find that in the code?