Sizing an Isolated Ground conductor!!!

Status
Not open for further replies.

sam34

Member
Location
Missouri
Hello every one, Could someone tell me what is the best approach to take to size an IGC (branch ckt's and feeders)? I have this situation where a multiple point of sale stations that required to have an Isolated ground.They are fed from 100A sub -panel back to MDP. I have been told to size it based on the same size of phase conductor?And also, can we daisy- chained the IG conductor?
Thank you,

Sam
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Re: Sizing an Isolated Ground conductor!!!

Originally posted by sam34:
And also, can we daisy- chained the IG conductor?
The IG has to go with the branch circuit wiring, so as long as you do that you could justify daisy chaining the IGs together, at least from a code perspective.

Personally, I see no reason to install IG receptacles at all. It adds cost and serves no useful purpose (IMHO).
 

sam34

Member
Location
Missouri
Re: Sizing an Isolated Ground conductor!!!

I agree with you, I don't see any use for IG but the owner have requested it because he thinks that will eliminate any noise for his equipment.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Sizing an Isolated Ground conductor!!!

Originally posted by sam34:
Hello every one, Could someone tell me what is the best approach to take to size an IGC (branch ckt's and feeders)?
Sam there is no need to size the IGs based on the feeder size, as has been said you need to use Table 250.122 but the IG will only be protecting 20 amp circuits, not the the feeder.

So at minimum you could use 12 AWG all the way back to your MDP.

In the past when it has not been specified for me I have used an 8 or 6 AWG for the run back to the bonding point.

It just looks strange to install a 12 AWG in a 225 amp feeder raceway. :D
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
Re: Sizing an Isolated Ground conductor!!!

Your question is irrelevant because in my opinion the IG from each receptacle should be run individually back to the MDP. Easy to do when you HR each receptacle from a main panel, not so easy from a sub panel.

I too see no reason IG's could make any difference here.

-Hal
 