Question 1: Is the generator 3 phase?
" 2: Is the ATS 1 ph or 3 ph ?
Some ATS units are 3 ph but are configured (wired) for 1 ph
so if it is a 3 ph gen and the ATS is 3 ph then yes, ATS just has to be configured and programmed for 3 phase
If the ATS is 1 ph then no
I find it hard to believe that a 22KW gen wound be 1 ph
so in that case you would need a 3 ph ATS to match the gen
they usually have a set 80% voltage drop before they start and transfer for the home units so it should still be good with 208v.One issue is, even if they are suppling a single phase panel, the generator control may see the 208 as under voltage, and may want to transfer not accept the utility voltages. Commercial transferswitches can be set to compensate for that, but the residential switches may be a fixed value. Have done it before with Genercraps, but all loads were 120 volt, so no issues of suppling 240 to 208 volt loads.
For optional standby systems pretty sure nothing. Legally required, don't think much from NEC but possibly from whatever code is behind needing a legally required standby system.I guess I'm worried about a brown out that might be a safety issue. And is there anywhere in the code that talks about this>