Would like to know whether it's best to shunt trip primary (13.8 kV) or secondary circuit breaker (2.4 kV) of building transformer under load?
 

charlie tuna

Senior Member
Location
Florida
Re: Shunt trip

i would say it is a matter of cost -- either shunt trip will be designed to handle the rated current flow. i would rather have it on the higher voltage breaker because it will be opening at a lower current..........
 

rick hart

Senior Member
Location
Dallas Texas
Re: Shunt trip

Since you probably already have relays on either, I would prefer a primary shunt trip. I assume the shunt trip is some sort of emergency power off?
 