Just double triple checking to make sure the sizing on all the other grounding conductors is done correct. They have ran 2 paralleled #4 copper egc’s between the 400a service disconnect to the ats, and also from the ats to the main distribution panel. As I understand these should be sized on 250.122 on the 400a breaker at the service disconnect and should be at least #3copper? They also have a #4 main bonding jumper inside of the service disconnect from ground to neutral lug. This should of been sized on 240.102(c) and should be at least #2 copper because the service entrance conductors are (2) paralleled 250kcmil aluminum conductors... “over 250 through 500 aluminum column” I just wanted to say again how much I appreciate everyone’s help, and patience! Thank you guys! If anyone sees issues with terminology I have used or sizes please let me know!