RUNNING PARALELL WIRES IN EMT

Status
Not open for further replies.

Duke1317

New member
Location
MIAMI FL USA
MAY I RUN 3-500KCMIL FOR ONE PHASE EXAMPLE:
3-4" EMT IN PARALELL WITH
PHASE A 3-500KCMIL 4" EMT
PHASE B 3-500KCMIL 4" EMT
PHASE C 3-500KCMIL 4" EMT
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
No you cannot have all of one phase in one conduit. There is an exception but it is with pvc conduit underground -- I believe

300.3(B)(1) said:
(1) Paralleled Installations. Conductors shall be permitted
to be run in parallel in accordance with the provisions of
310.10(H). The requirement to run all circuit conductors
within the same raceway, auxiliary gutter, cable tray, trench,
cable, or cord shall apply separately to each portion of the
paralleled installation, and the equipment grounding conductors
shall comply with the provisions of 250.122. Parallel runs
in cable tray shall comply with the provisions of 392.20(C).
Exception: Conductors installed in nonmetallic raceways
run underground shall be permitted to be arranged as isolated
phase installations. The raceways shall be installed in
close proximity, and the conductors shall comply with the
provisions of 300.20(B).
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I might add that even if you do use PVC conduit, you have to make provisions in the event the conduits terminate in a metal enclosure.
In the event these are service conductors it would be a good idea to check with your POCO as some of them prohibit such installations.
 

kwired

Electron manager
Location
NE Nebraska
There is a fairly recent thread where the OP had encountered just what you described - IIRC same raceway and conductor sizes even.

He had some heating issues at that install.
 

iwire

Moderator
Staff member
Location
Massachusetts
Here is a example of applying the exception Dennis mentioned.

Als_Isolated_Phase.JPG



While fine in PVC underground it isa no go with EMT.
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
Why is it OK with PVC?

A) Is it because the PVC will minimize the heat transfer and other combustable material touching the conduit will not be a fire hazard?

or

B) The magnetic heating is not an issue because the conduit is not metal?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
:)


On longer posts I make more errors.. on that one I had a 50-50 chance.
 

kwired

Electron manager
Location
NE Nebraska
Why is it OK with PVC?

A) Is it because the PVC will minimize the heat transfer and other combustable material touching the conduit will not be a fire hazard?

or

B) The magnetic heating is not an issue because the conduit is not metal?

Not only is it not metal, it is not steel. Aluminum conduit possibly would have some problems but not as much as a steel conduit.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
Would there be any point in taking advantage of the PVC exception? Is it somehow easier run all of one phase in a conduit? (I mean some advantage besides having people who don't quite know what they are doing be able to 'get away with' a code compliant install).
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Would there be any point in taking advantage of the PVC exception? Is it somehow easier run all of one phase in a conduit? (I mean some advantage besides having people who don't quite know what they are doing be able to 'get away with' a code compliant install).

Typically it makes it easier to keep the paralleled conductors close to the same length and it makes it much easier to terminate.

Roger
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
MAY I RUN 3-500KCMIL FOR ONE PHASE EXAMPLE:
3-4" EMT IN PARALELL WITH
PHASE A 3-500KCMIL 4" EMT
PHASE B 3-500KCMIL 4" EMT
PHASE C 3-500KCMIL 4" EMT

Does the term "inductive heating" ring a bell?

Roger
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Would there be any point in taking advantage of the PVC exception? Is it somehow easier run all of one phase in a conduit? (I mean some advantage besides having people who don't quite know what they are doing be able to 'get away with' a code compliant install).

FWIW, for an existing duct bank, it allows you to avoid the need for all of the parallel raceways to be the same size.
 