How does article 695 apply ?

Tapping ahead of a pedistal breaker is not possible.

Have many developments requiring fire sprinkler and pump systems. Need sujestions for safe instalions.
 

tom baker

First Chief Moderator
Staff member
Re: Residential fire pumps

Are the residential fire pumps required by the fire dept AHJ and hence installed per 695?
You would have to have a tap ahead of the service. I was thinking a large junction box that would allow taps to be made and then run straight to the fire pump controller.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Residential fire pumps

I think you need to look at a copy of NFPA 13D (Standard for theInstallation of Sprinkler Systems in One- and Two-Family Dwellings and Manufactured Homes). I do not have a copy, but know that many of the installation requirements in 13D are not as strigient as in 13 (Standard for theInstallation of Sprinkler Systems).
Don
 

websparky

Senior Member
Location
Cleveland, Ohio
Re: Residential fire pumps

NFPA 13 is correct. However, it refers you to NFPA 20 for water supplies which includes pumps.
Basically it says a pump is not always required but if one is used, there are a few differences in residential pump wiring but, it must follow NFPA 70 Article 695 for the most part.

Typically an installer of a sprinkler system must be licensed. No?
 