This might sound dumb, I'm old school. I have a 40hp air compressor that is set up with VFD controls. I've never been able to get it to work. I don't need or want the VFD. Can I make it work like a non-VFD compressor and if so, how? THanks
Thats pretty common with techs. I second the others call around and get a local sparky to give you a consultation on the VFD. Also if you post the link to the make / model of the unit on here you might get some help on here if its just a programing issue and not a DIY wiring issue.Some additional info: this is a brand new USAir compressor 40hp, 480v. connecting to a 100 amp disco.
A couple of compressed air techs I have talked to don't wan't to mess with it because they don't know the brand and want to sell me their own brand of compressor.
Just from experience;
Unless the VFD is roughly 3x the size of the motor, it will not be able to start a compressor if the unload valve is not open to atmosphere. Even though it is new, there may be an issue with the unload solenoid that means it is not engaging. The same could be true of a mechanical unloader. If they don’t unload for startup, the VFD just goes into current limit to protect itself until it shuts down on stalled motor.
Some additional info: this is a brand new USAir compressor 40hp, 480v. connecting to a 100 amp disco.
Are you possibly in the wrong forum? Most here have some experience of VFDs - they have been around for decades.This might sound dumb, I'm old school. I have a 40hp air compressor that is set up with VFD controls. I've never been able to get it to work. I don't need or want the VFD. Can I make it work like a non-VFD compressor and if so, how? THanks
Sorry, still here. extremely busy. wearing a lot of hats right now.... talking to the company you bought it from- to make it work.
You still haven't told us what the problem is.
-Hal
VFDs don't just "turn on" out of the box, they need programming and methods to tell them to turn on and off, what speed to run etc. etc. If you bought a cheap machine from FleaBay and it was not properly set up, the seller should be helping you. If you can't get that help, the lesson learned here might be "you get what you pay for"...
One would hope….Yeah, the VFD would have been setup properly by the manufacturer, …
I found this machine on Ebay. My 25 HP screw Kaeser unit was not keeping up so I had them quote me on a 40hp one. Way too high for me, so the one I found on Ebay seemed almost too good to be true. When I connected to power and tried to turn on just to check rotation, nothing happened. I assumed it was a setting on the VFD that was off so I tried to call them and could not get through.