Actually I was think in terms of reducing the cost of a customer owned installation.

Service point at the 'road', then customer owned feeder crossing the property.

If the customer owned feeder is designed to carry 2A at 650V DC on a continuous basis rather than 100A at 240V very infrequently, then that feeder conductor could be very small indeed.

-Jon
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
Actually I was think in terms of reducing the cost of a customer owned installation.

Service point at the 'road', then customer owned feeder crossing the property.

If the customer owned feeder is designed to carry 2A at 650V DC on a continuous basis rather than 100A at 240V very infrequently, then that feeder conductor could be very small indeed.

-Jon
Well, 2 amps at 650VDC sounds pretty puny for a commercial or industrial installation regardless of how much battery storage you have, and around here, the POCO owns everything to the weatherhead, so no advantage to a residential customer.
 

pv_n00b

Senior Member
Location
CA, USA
Occupation
Professional Electrical Engineer
I think winnie's point was using batteries to smooth the demand as far as the POCO is concerned, not in conjunction with PV.
Sure, take away the PV. The utility service has to be able to supply the load if the BESS fails, so there is no option to undersize any of it. It's an interesting idea, just not feasible in the real world.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
Sure, take away the PV. The utility service has to be able to supply the load if the BESS fails, so there is no option to undersize any of it. It's an interesting idea, just not feasible in the real world.
It's an interesting though experiment about forcing load management onto the customer, rather than the POCO having to cover load changes over the day, if you're willing to tell customers that they are SOL if the batteries fail.
 

retirede

Senior Member
Location
Illinois
Sure, take away the PV. The utility service has to be able to supply the load if the BESS fails, so there is no option to undersize any of it. It's an interesting idea, just not feasible in the real world.

In his example, the only load that can possibly be served by the utility is a 1.5 KW DC power supply. Nothing else is capable of being powered from the utility.
 