Raceways

Status
Not open for further replies.

hodie

New member
I am working on a school in ky and have 8 electrical panels in the mechanical room, I need to get 30 circuits out of each panel and distribute them to different rooms, I am pressed for enough room to keep the 3 circuits 1 neutral in any 1 condiut so was wondering if i can run a 8x8 wireway to distribute my circuits to varies locations remember I have 8 panels all 120/208 3ph
 

stew

Senior Member
Re: Raceways

even given what nick says you are much better off to just use pipe large enough to give you reas9onable pulling room and derate the conductors. Assuming thhn use the 90 degree table as your starting point and apply 310.15(B)(2)(a) as needed.3 boats of thhn #12 still gives you 21 amps to work with.

[ June 29, 2004, 02:58 PM: Message edited by: stew ]
 