Attached sketch left shows two tenant spaces tenant 1 and tenant 2. Panel A is in tenant 1 space and Panel B in tenant 2 space.
Later tenant #2 moves and tenant #1 expands to tenant #2 space as shown on middle Floor plan one tenant with door between spaces attached sketch. However Panel A and Panel B are not moved. The power riser is shown to the right in sketch. Panels A and B are each fed from 200A meter disconnect grouped as shown. Meter stack has 800A main service disconnect.
Question is their a requirement in code to group Panel A and Panel B together when their is only one tenant occupying both spaces or can it be separate as shown on middle floor plan sketch?
Later tenant #2 moves and tenant #1 expands to tenant #2 space as shown on middle Floor plan one tenant with door between spaces attached sketch. However Panel A and Panel B are not moved. The power riser is shown to the right in sketch. Panels A and B are each fed from 200A meter disconnect grouped as shown. Meter stack has 800A main service disconnect.
Question is their a requirement in code to group Panel A and Panel B together when their is only one tenant occupying both spaces or can it be separate as shown on middle floor plan sketch?