Question about 410.130(G)1 - (G3)

Dan120

Member
Location
Florida
Occupation
Journeyman Electrician
Hello, section 410.130(G)(1) states that fluorescent luminaries that utilize double ended lamps and contain ballast that can be services must have a disconnect.
My question is, as of 410.130G(3) does this mean a regular toggle switch can serve as the disconnecting means? Also does this only relate to non-dwelling locations?
I know fluorescent lamps are facing out so it’s not as relevant anymore but I will still like to know. Thanks
2017 NEC
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
Nothing in code indicates any limits to non-dwelling or dwelling so would be applicable to both. a switch insight of fixture is allowed if controlling only the one fixture and not part of a MWBC then it must also break all conductors including the grounded conductor. I know no toggle that does that.
Rather than mess with a switch just use something like this. it provides the needed "disconnect" compliant with Exception 3.

1697712483547.png 1697713011143.png

1697713931686.png
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Nothing in code indicates any limits to non-dwelling or dwelling so would be applicable to both. a switch insight of fixture is allowed if controlling only the one fixture and not part of a MWBC then it must also break all conductors including the grounded conductor. I know no toggle that does that.
Rather than mess with a switch just use something like this. it provides the needed "disconnect" compliant with Exception 3.
(1) General.
In indoor locations other than dwellings and associated accessory structures,
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Hello, section 410.130(G)(1) states that fluorescent luminaries that utilize double ended lamps and contain ballast that can be services must have a disconnect.
My question is, as of 410.130G(3) does this mean a regular toggle switch can serve as the disconnecting means? Also does this only relate to non-dwelling locations?
I know fluorescent lamps are facing out so it’s not as relevant anymore but I will still like to know. Thanks
2017 NEC
It can where the switch is within sight of the luminaries.
 

Dan120

Member
Location
Florida
Occupation
Journeyman Electrician
Other than dwelling unit means = anything outside of dwelling unit/not applicable to a dwelling unit?
I understand now about the switch only permitted if not part of MWBC and within sight of the luminaries, Thanks
 