Does 250.66(A) mean that if I only have ground rods the maximum size grounding electrode conductor required is #6? If I have a second ground rod I don't have to size the connection as a bonding jumper? 250.66(A) says ".....connected to a single or multiple rod, pipe or plate electrode(s)...." so I can ignore Table 250.66?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
The table does not apply to rods however, you can use it for #2 or smaller.

Roger
 

tom baker

First Chief Moderator
Staff member
Section 250.66 covers the size of GECS, and parts A, B, C gives the sizes to ground rods, conc encased electrodes and ground rings.
So yes 250.66(A) allows a 6 AWG to a ground rod. The connection to a second ground rod is a bonding jumper and and is sized per 250.66(A)
 

kwired

Electron manager
Location
NE Nebraska
2014 appears to be when wording was changed and does clarify this

"Where the grounding electrode conductor is connected to a single or multiple rod, pipe, or plate electrode(s)....

bold part was added.