The phrase "an assembly, together with its overcurrent device(s)" to me covers an assembly with 0 or more OCPD, and is not restricted to assemblies with 1 or more OCPD. At best it is ambiguous. But the physics supports my interpretation, as the 125% factor for continuous loads is only due to OCPD limitations.The exception does not specify "or lack thereof where not required". It only refers to 100% continuous duty rated equipment with overcurrent devices.
Cheers, Wayne