Well i always thought I understood PV wire sizing, but as y'all know it gets a bit complex.
I am combining two PV strings on roof. Each string is 10.5 A Isc each = 21 A Isc combined.
There are existing #10 THHN conductors in conduit from roof to inverter. I would like to use those for labor saving.
Can I?
Overall, I would do the calcs like so:
De-rate wire ampacity down and multiply current up, then compare. Current must be less than equal to ampacity.
Specifically,
A. AMPACITY
Start with 40A ampacity to derate #10 THHN wire.
2 de-rates to consider:
-- Only 2 CCC in conduit, so no derate for # of wires in raceway.
-- Ambient TEMP: Average high Temps are just about 70-80F here, so no derate. (I recall it is average high temps that are to be used. Am i right on this? or record high Temp must be applied? Big difference!)
===> 40A x 1.0 x 1.0 = 40 A allowable ampacity (although ultimately 30A max allowed by NEC in end no matter what)
Now....can I further de-rate the 40A ampacity by 0.8 PV use factor - rather than multiply the Isc and continuous use factor by 1.25?
That gives me 32A allowable. This of course gets knocked to 30A absolute max allowable.
B. CURRENT
I multiply 21 A Isc by 1.25 continuous use factor = 26.25 A.
This is under the above 30A, so I am golden.
Otherwise if I must multiply by 1.56 (1.25 continuous and 1.25 PV use factors), then 1.25 x 1.25 x 21 A pushes me over 30A by a smidge. (1.56 x 21 A = 32.81 A) Ok.... by 2.81 smidges.
My recent reading says the 1.56 had been implied by the NEC, but not quite that simple..... and has been since clarified.
In other words, there is something about applying the 1.25 factors separately one at a time, but I never quite got that.
Any insight appreciated gents!
I am combining two PV strings on roof. Each string is 10.5 A Isc each = 21 A Isc combined.
There are existing #10 THHN conductors in conduit from roof to inverter. I would like to use those for labor saving.
Can I?
Overall, I would do the calcs like so:
De-rate wire ampacity down and multiply current up, then compare. Current must be less than equal to ampacity.
Specifically,
A. AMPACITY
Start with 40A ampacity to derate #10 THHN wire.
2 de-rates to consider:
-- Only 2 CCC in conduit, so no derate for # of wires in raceway.
-- Ambient TEMP: Average high Temps are just about 70-80F here, so no derate. (I recall it is average high temps that are to be used. Am i right on this? or record high Temp must be applied? Big difference!)
===> 40A x 1.0 x 1.0 = 40 A allowable ampacity (although ultimately 30A max allowed by NEC in end no matter what)
Now....can I further de-rate the 40A ampacity by 0.8 PV use factor - rather than multiply the Isc and continuous use factor by 1.25?
That gives me 32A allowable. This of course gets knocked to 30A absolute max allowable.
B. CURRENT
I multiply 21 A Isc by 1.25 continuous use factor = 26.25 A.
This is under the above 30A, so I am golden.
Otherwise if I must multiply by 1.56 (1.25 continuous and 1.25 PV use factors), then 1.25 x 1.25 x 21 A pushes me over 30A by a smidge. (1.56 x 21 A = 32.81 A) Ok.... by 2.81 smidges.
My recent reading says the 1.56 had been implied by the NEC, but not quite that simple..... and has been since clarified.
In other words, there is something about applying the 1.25 factors separately one at a time, but I never quite got that.
Any insight appreciated gents!