Looking at a BIPV project, where pv source circuit conductors are being proposed as running inside a custom aluminum extrusion going east to west, this portion is left open and accessible, and should be of no concern.
Where I am curious, and expressing concern, is where those conductors enter an also custom aluminum extrusion that essentially runs up a rafter, and that raceway is then closed of by a removable piece that is screwed in.
There is no concern of damage to the conductors where the secondary piece screws to the aluminum mullion, as the design of the extrusion makes it impossible.
Without you seeing the design of the extrusion, can you think of any issues we may face with respect to being not compliant with NEC code? Thanks in advance.