Rick A
Member
- Location
- San Diego, CA
- Occupation
- Inspector
I have a question about requirements for a PV system on an attached condominium in Southern California. Picture eight single story units in a building all with the same floor plan, four stacked over four others. The upper four units are the ones with direct attic/roof access. The electrical and gas meters are all grouped together only on one end of the building.
Each unit has a 125A panel inside and a 50A main breaker at the utility meter. There's no other disconnect outside the unit except the main 50A breaker…no switched disconnect next to the meter, nothing. The panel in each unit is fed with 6 AWG SEC conductors with some of those being right next to the meter (maybe 25 feet) and others approaching 150 feet for units at the far end.
I’m familiar with how single family dwelling PV systems are tied in but in this case where would the back-fed breaker need to be located? Could it go right into the panel in the unit? Would a disconnect need to be added at the meter in addition to the main breaker? I guess the distance between the panel and the meter are confusing me and that’s there’s no outdoor service panel access.
Each unit has a 125A panel inside and a 50A main breaker at the utility meter. There's no other disconnect outside the unit except the main 50A breaker…no switched disconnect next to the meter, nothing. The panel in each unit is fed with 6 AWG SEC conductors with some of those being right next to the meter (maybe 25 feet) and others approaching 150 feet for units at the far end.
I’m familiar with how single family dwelling PV systems are tied in but in this case where would the back-fed breaker need to be located? Could it go right into the panel in the unit? Would a disconnect need to be added at the meter in addition to the main breaker? I guess the distance between the panel and the meter are confusing me and that’s there’s no outdoor service panel access.