Stevenfyeager

Senior Member
Location
United States, Indiana
Occupation
electrical contractor
I have a customer's Gen. Switch panel that labels GE THQL as compatible. Its 25 years old. AFCI GE breakers have THQL model letters followed by 1122 plus other letters. You think the elec inspector will accept this ? This state requires everything AFCI. Thanks
 

growler

Senior Member
Location
Atlanta,GA
I have a customer's Gen. Switch panel that labels GE THQL as compatible.

Make sure the inspector is aware this is a listed replacement and don't expect him/her/it to figure it out. If I wasn't going to be there for the inspection I would use a high liter and leave a note explaining what I was doing.
 