How would one bond this heat exchanger for a commercial pool? There is no lug on the unit and most of the external components are powder coated. My thought was to put a pipe clamp on the stainless steel nipple that transitions to the plastic pipe. The copper piping is the feed from the boiler.
Pool Heat Exchanger 001.jpg
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
There’s nothing electrical going on inside that exchanger we can’t see from the pic, right ? From a bonding safety standpoint I don’t think you are required to bond the exchanger.


Sent from my iPhone using Tapatalk
 

SSDriver

Senior Member
Location
California
Occupation
Electrician
We usually just bond the boiler that is feeding the heat exchanger. I have never had to bond the plate exchangers before.
 