pool bonding fail

Status
Not open for further replies.

JakeS

Member
Location
inland empire
Occupation
Inspector 1
I was looking at the bonding on a pool today, the contractor buried the 4 points from the pool shell when they did the shotcrete. Instead of chipping shotcrete away, finding rebar and clamping on at 4 points around the pool the contractor tied the copper around a rock at 4 corners buried it a foot deep compacted the soil in around it then clamped it on to the bonding wire around the pool. It blew my mind, just thought id share.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
He will know next time to use a bigger rock so you can't pull it up :p
 