Hi. First post here....
Tomorrow will be an interesting day as I'm borrowing a friendly electrician and his fluke meter to see what's going on with my three phase install.
What we have:
UK based Three-phase four wire PME (Protective multiple earth) supply. 100 amps per phase.
1 phase with pretty much all of the normal 'house' loads (lighting, socket circuits, utility room, immersion coil for the heat store etc.)
1 phase with about 94 amps of convection heaters (nobo as)
1 phase with a 96 amp (several 7Kw elements) tankless water heater which only draws power when someone opens a hot tap.
The 'house' phase has several loads (computers) that I think are likely to cause some harmonics but the trouble's really started now we installed the water heater.....
When it's drawing power you can visably see the house lights pulse. This is especially visible on the 500 watts of dimable lights in the new bathroom if you turn them nearly off.
I'm hoping someone can tell me if this is likely to be simply the cause of my very unbalanced loads being aggrevated even more. Does anyone have suggestions on how I can, cheaply, clean my system up, improve the power factor (save me money), and stop the lights flickering?!
Tomorrow afternoon I should know what the neutrals are doing (hopefully not getting warm), and what, if any, harmonics are present. So I should be able to answer questions.
Finally, can I assume, that the likes of www.liebert.com 's DataWave and www.powerperfector.com products are going to be far too expensive for a SOHO user? I note that most of the manufactures who produce Power Factor correction and harmonic filtering tend to slag off other methods whilst saying their 'patented' method is best. It makes it very difficult to figure out, as a lay person, what's actually 'for real'. Acme's I-Trap and the Harmonix product look like they might do the job too.
Finally I thought you might all get a kick out of a circuit monitoring project I found recently that I plan to implement so I can see exactly what's costing me the most round the house (http://www.kondra.com/circuit/circuit.html)
Cheers,
sk
ps. Hopefully when I've got everything sorted I will add a 15Kw net connected wind turbine
Tomorrow will be an interesting day as I'm borrowing a friendly electrician and his fluke meter to see what's going on with my three phase install.
What we have:
UK based Three-phase four wire PME (Protective multiple earth) supply. 100 amps per phase.
1 phase with pretty much all of the normal 'house' loads (lighting, socket circuits, utility room, immersion coil for the heat store etc.)
1 phase with about 94 amps of convection heaters (nobo as)
1 phase with a 96 amp (several 7Kw elements) tankless water heater which only draws power when someone opens a hot tap.
The 'house' phase has several loads (computers) that I think are likely to cause some harmonics but the trouble's really started now we installed the water heater.....
When it's drawing power you can visably see the house lights pulse. This is especially visible on the 500 watts of dimable lights in the new bathroom if you turn them nearly off.
I'm hoping someone can tell me if this is likely to be simply the cause of my very unbalanced loads being aggrevated even more. Does anyone have suggestions on how I can, cheaply, clean my system up, improve the power factor (save me money), and stop the lights flickering?!
Tomorrow afternoon I should know what the neutrals are doing (hopefully not getting warm), and what, if any, harmonics are present. So I should be able to answer questions.
Finally, can I assume, that the likes of www.liebert.com 's DataWave and www.powerperfector.com products are going to be far too expensive for a SOHO user? I note that most of the manufactures who produce Power Factor correction and harmonic filtering tend to slag off other methods whilst saying their 'patented' method is best. It makes it very difficult to figure out, as a lay person, what's actually 'for real'. Acme's I-Trap and the Harmonix product look like they might do the job too.
Finally I thought you might all get a kick out of a circuit monitoring project I found recently that I plan to implement so I can see exactly what's costing me the most round the house (http://www.kondra.com/circuit/circuit.html)
Cheers,
sk
ps. Hopefully when I've got everything sorted I will add a 15Kw net connected wind turbine