parallel neutral

Status
Not open for further replies.

domnic

Senior Member
Occupation
Electrical Contractor
What hazard cud parallel neutrals cause . ( not hots just neutrals in a 100 amp service a#6 and #3)
 

mikeames

Senior Member
Location
Germantown MD
Occupation
Teacher - Master Electrician - 2017 NEC
In reality it would be unnoticed, once installed, but its not legal and with a #6 and a #3 its silly and not smart. Paralleled conductors must be the same size, material, and insulation type. Additionally the minimum size allowed to be paralleled is 1/0 (310.10-H)
 
Last edited:

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
The "hazard" is that half of the current will flow on the smaller conductor.

Can you give us more detail? Why would the #6 land in both enclosures?
 

domnic

Senior Member
Occupation
Electrical Contractor
The "hazard" is that half of the current will flow on the smaller conductor.

Can you give us more detail? Why would the #6 land in both enclosures?
The inspector rule when you run pvc on a service. (on down run)
 

domnic

Senior Member
Occupation
Electrical Contractor
Parallel #6 and #3 the #6 will cray 1/2 the load. ( 100 amps the #3 50 amps the #6 50 amps ? )
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
The inspector rule when you run pvc on a service. (on down run)
He's exactly wrong. To quote myself:


The basics: On the line side of whichever enclosure houses the main disconnect (and ignoring the meter), there is no EGC, there is only the neutral.

The main disconnect is where the premises grounding system begins as separate conductors, and its connection to the service neutral is the main bonding conductor. The grounding electrodes (rod(s), water pipe, building steel, etc.) must also connect to the service neutral at (or before) this point.

Any circuits leaving this enclosure, whether branch circuits or feeders, must include an EGC separate from the neutral (if there is one), and said neutral should never be bonded to ground again. Except for switching, fusing, etc., we treat the neutral as we would any ungrounded (hot) conductor.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The 6 AWG will not carry half of the circuit current. The current will divide in inverse proportion to the impedances of the two conductors. While this is a code violation, there is no real world hazard here unless the 3 AWG would become open. The current split will be ~33% on the 6AWG and 68% on the 3AWG.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
200604-1333 EDT

LarryFine:

Your comment in post #6 is very wrong.

Essentially you have two resistors in parallel. One resistor is approximately 1/2 the resistance of the other. Both resistors have the same voltage applied. The power dissipated in the higher resistance is about 1/4 that of the lower resistance.

An approximate rule of thumb is that resistance changes by a factor of about 2 for a change of 3 in wire size.

Power transfer (power dissipation) from a wire is a complex function dependent upon many factors.

As an example the fusing current for copper wire for two sizes is:

#10 1 ohm/1000 ft 333 A.
#16 4 ohm/1000 ft 147 A.
A 4 to 1 resistance change, and a 2.26 ratio of currrents.
Four (4) #16 in parallel would have a fusing currrent of 587 A. Much better than 333 A.

.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Essentially you have two resistors in parallel. One resistor is approximately 1/2 the resistance of the other. Both resistors have the same voltage applied. The power dissipated in the higher resistance is about 1/4 that of the lower resistance.
Your theory is spot on, but in my opinion, the actual measured current through 1-foot pieces of #3 and #6 will not divide in the same proportions. An experiment with a clamp-on meter and a substantial load would be in order.

A friend who is an EE with power-distribution experience once told me that they switched line taps from dual to single crimp because some of the line current diverged through the stirrup:

1591383758125.png 1591383771666.png
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
n
200604-1333 EDT

LarryFine:

Your comment in post #6 is very wrong.

Essentially you have two resistors in parallel. One resistor is approximately 1/2 the resistance of the other. Both resistors have the same voltage applied. The power dissipated in the higher resistance is about 1/4 that of the lower resistance.
...
Since both resistors have the same voltage applied the higher resistance will dissipate one half the power of the lower resistance, with one dissipating 1/3 of the total power and the other dissipating 2/3/
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
200604-1700 EDT

Gold Digger:

You are correct. I guess I was half asleep when I did some form of calculation in my head. I^2*R vs (I/2)^2*R*2. V^2/R vs V^2/(2*R) would have avoided the problem.

However, the fusing current values were from a table in the ITT Reference Data for Radio Engineers 4th Edition handbook, and are probably reasonably correct.

.
 