OSHA mandated as-builts

Status
Not open for further replies.

W6SJK

Senior Member
I seem to recall discussion years ago, possibly in EC&M, that OSHA required up-to-date as-builts for facilities. Is that true or was I dreamin'? Can't find it in a search of the OSHA site. TNX Steve
 

kingpb

Senior Member
Location
SE USA as far as you can go
Occupation
Engineer, Registered
But I think with all the arc flash stuff, it's going to require facilities to finally pony-up and pay to have someone do as-builts.

You can pay me now, or you can pay me a lot more later!
 

boater bill

Senior Member
Location
Cape Coral, Fl.
The Florida Board of Professional Engineers is considering requiring engineers to provide the as-builts and O&M manuals for public and governmental facilities. This is fine as long as someone pays for it. My experience is the installing contractor knows more about the installed equipment and has the access to the installed equipment than the engineer. The engineers spec is typically going to call out for several acceptable manufacturers, but the installing contractor has the final decision. Shop drawings do not a O&M manual make.

Any one else with thoughts regarding this?
 

boater bill

Senior Member
Location
Cape Coral, Fl.
Manufacturer's data of the installed equipment, operation of a system such as an HVAC control system, maintenence data and schedules. Items the building owner would need to know for basic trouble shooting.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
As part of their Process Safety Management (PSM - that's PMS out of phase) FedOSHA requires single-lines and electrical area classification documentation to be kept up to date. Within their scope of enforcing the NEC/70E they require up to date panel schedules.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
boater bill said:
Manufacturer's data of the installed equipment, operation of a system such as an HVAC control system, maintenence data and schedules. Items the building owner would need to know for basic trouble shooting.

stuff that the contractor would get from whomever they bought the stuff from, and should trun over to the building owner.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Bob A.
I think that in PSM areas, you are also required to keep the flow sheets or PID drawings up to date.
Don
 

tlaidman

Member
Location
Cleveland Ohio
As I said for an earlier post the use of the term as built can get you into trouble legally. Use the term record drawing it prevents you from problems if it is not exactly as built.
 

W6SJK

Senior Member
rbalex said:
As part of their Process Safety Management (PSM - that's PMS out of phase) FedOSHA requires single-lines and electrical area classification documentation to be kept up to date. Within their scope of enforcing the NEC/70E they require up to date panel schedules.

Thanks, that must be what I was thinking of. And yes, I use the term record drawings in contracts. I was using as-builts as a more common if not slang term. Besides, I wasn't referring to the contractor and his as-builts. I meant that the owner of the facility had the duty to keep drawings up to date and on file after the CO. Thanks to all for the replies.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
You're right of course Don; I was simply listing items generally considered "electrical" in nature.
 

PrimeEdge

New member
Osha

Osha

OSHA's purpose is to save lives, prevent workplace injuries and illnesses, and protect the health of all America's workers. I think there are some regulations in place which require an update to Electrical Panel Schedules and curcuit designations. As-built drawings are not an OSHA requirments at this point.