I've been asked to bid on a service upgrade. When I got to the job i noticed that the service is a main lug with a 60 amp lighting main. There is no disconnect outside or main on the panel.
The owner does not know what size service he currently has. There is no information on the panel. Wire size is 2/0 CU. I now see that he does not need to up the service, just a panel change.
I noticed a few large lines in this panel and asked as to the nature, Dryer, Elec. Range, A/C etc... I was told that there is a sub panel in the attic that has been converted into living space. I asked to see this panel and it is in the bathroom. This panel is feed with 3/4" Greenfield- 2 hots 1 neutral, that?s it. There is also a 50 amp feed to the detached garage. I have not been outside to look in the garage, more than likely a panel there as well.
Owner wants a 150 amp panel. I worked up a price and gave it to him, I'm about $150.00 more that the others he has talked with prior. The owner told me neither of the others looking at this job looked further than the panel in the basement, the one being change. I told him I was pulling a permit and the Inspector may want to know what these feeds go to.
If the Inspector looks more closely they may want to know what theses feed go and would more than likely Red Tag the entire job. I told the owner that the panel in the bathroom has to moved and he said he would do it only if made to by the Inspector and HE would do it.
All of that said, I'm thinking I want to turn this job down, am I way off base here? I welcome any thoughts.
Thanks for indulging my dissertation.
Norb
The owner does not know what size service he currently has. There is no information on the panel. Wire size is 2/0 CU. I now see that he does not need to up the service, just a panel change.
I noticed a few large lines in this panel and asked as to the nature, Dryer, Elec. Range, A/C etc... I was told that there is a sub panel in the attic that has been converted into living space. I asked to see this panel and it is in the bathroom. This panel is feed with 3/4" Greenfield- 2 hots 1 neutral, that?s it. There is also a 50 amp feed to the detached garage. I have not been outside to look in the garage, more than likely a panel there as well.
Owner wants a 150 amp panel. I worked up a price and gave it to him, I'm about $150.00 more that the others he has talked with prior. The owner told me neither of the others looking at this job looked further than the panel in the basement, the one being change. I told him I was pulling a permit and the Inspector may want to know what these feeds go to.
If the Inspector looks more closely they may want to know what theses feed go and would more than likely Red Tag the entire job. I told the owner that the panel in the bathroom has to moved and he said he would do it only if made to by the Inspector and HE would do it.
All of that said, I'm thinking I want to turn this job down, am I way off base here? I welcome any thoughts.
Thanks for indulging my dissertation.