Nominal Voltage

Status
Not open for further replies.

fmtjfw

Senior Member
The NEC contains 2744 sentences that contain volt, voltage, and V. Some of the V are false positives (part V, Volume ...). 317 sentences contain nominal. The use of the word nominal does not appear to have a particular pattern when it is found in connection to voltage. Having some voltages marked as nominal and others not marked when both are intended to be nominal, leads to confusion


Some of the voltage references are for exact voltages. This is true for most "limit" specifications such as "the voltage shall not exceed 42.4 volts".


The specification of 600 volts, which is a utilization voltage, and 1000 volts, which is the "new" 600 volts, is problematical. I have chosen to treat these references as nominal.


I propose that the NEC indicate that all voltages listed in it are nominal, unless specifically marked actual This would rid the document of uncertainty as to whether or not a given voltage specification was actual or nominal.


Also add a table that indicates that the three groups of nominal voltages refer to the same thing: for instance 125/250 device rating, 120/240 load rating, and 115/230 motor rating.


The NEC contains the following different voltage references:
actual (exact)nominal (utilization)

8
10
12.4
15
21.2
24
24.8
30
42
42.4
50
60
65
80
100
132
150
200
300
301
350
600*
750
900


1080
1280
1530
2000*
2001
5000
15000
35000
50000

90
110
115
120
120/240
180
200
208
208Y/120
220
230
240
440
480
480Y/277
500
550
600
600Y/347


1000
2300
2400
4160
7200
7500
13800
14400
15000
23000
34500
46000
69000
115000
138000
230000


* occasionally marked nominal.


I propose the following steps:

  • [LI]Delete the word nominal together with comma(s) associated with it.[/LI]
    [LI]Add definition Voltage, Actual indicating it means a precise value associated with a hard limit.[/LI]
    [LI]Restore the nominals that were not associated with voltage.[/LI]
    [LI]Insert actual modifying voltage as needed.
 
Status