"CIRCUIT BREAKERS WITH EQUIPMENT GROUND-FAULT PROTECTION (DIYA)
USE AND INSTALLATION
This category covers combination circuit breaker and equipment ground fault protective devices designed to serve the dual function of providing overcurrent protection, and ground fault protection for equipment, as required by Articles 426 and 427 of NFPA 70, ??National Electrical Code?? (NEC).
A circuit breaker and equipment ground fault device is intended to be installed only on grounded alternating current systems in accordance with the NEC.
.(1) These devices are intended to be installed in new or existing panel-boards or the like.
.(2) The equipment ground fault protection trip level is marked on the devices.
.(3) These devices are suitable for use on systems where the voltage does not exceed the rating on the device.
.(4) A two-wire device is not suitable for use in a multiwire branch cir-cuit as defined in the NEC.
.(5) These devices are marked so that they can be distinguished from a circuit breaker and ground fault circuit interrupter.
.(6) These devices may have any voltage rating that is acceptable for a circuit breaker.
RELATED PRODUCTS
See Circuit Breakers, Molded-case and Circuit Breaker Enclosures (DIVQ).
ADDITIONAL INFORMATION
For additional information, see Circuit Breakers (DHJR) and Electrical Equipment for Use in Ordinary Locations (AALZ).
REQUIREMENTS
The basic standards used to investigate products in this category are UL 489, ??Molded-Case Circuit Breakers, Molded-Case Switches and Circuit Breaker Enclosures?? and UL 1053, ??Ground-Fault Sensing and Relaying Equipment.??
UL MARK
The Listing Mark of Underwriters Laboratories Inc. on the product is the only method provided by UL to identify products manufactured under its Listing and Follow-Up Service. The Listing Mark for these prod-ucts includes the UL symbol (as illustrated in the Introduction of this Directory) together with the word ??LISTED,?? a control number, and the product name ??Circuit Breaker With Equipment Ground Fault Protection?? or the abbreviation ??C.B. W/EQ.GFP.??
"