Sometimes my mind questions my mind.
Situation: 2000 amp service, fed by (6) runs of 500kcmil Cu. No Neutral load.
Pad has a neutral so I know from 250.24(C) that I have to install a neutral to my service gear. If I read correctly, the neutral in each conduit must be 375 kcmil (12-1/2% of sum of ungrounded conductors). Am I correct?
Situation: 2000 amp service, fed by (6) runs of 500kcmil Cu. No Neutral load.
Pad has a neutral so I know from 250.24(C) that I have to install a neutral to my service gear. If I read correctly, the neutral in each conduit must be 375 kcmil (12-1/2% of sum of ungrounded conductors). Am I correct?