Having some issues with a couple inverters on a residential site. We've had two inverters fail now, both with the same issue.
Referencing the manual for the error code says "For all 3-phase inverters, especially in new installations, (but also in existing installations, depending on the grid quality on site) the error often appears in connection with a shifted neutral point / star point. This can be caused by larger consumers on the grid, for example air conditioners, pumps, large motors and lifts or by a faulty installation."
Everything I'm reading on neutral shifting indicates this is an issue with three phase sites, but we are 240 split phase. Anyone know if neutral shifting can occur on split phase services? Or is this problem only seen on three phase services?
The customer does have several heat pumps wired up without neutrals, as well as a welder that doesn't use a neutral. Also, we have another customer with the same inverters that is across the street, and they haven't had any issues with their system.
Referencing the manual for the error code says "For all 3-phase inverters, especially in new installations, (but also in existing installations, depending on the grid quality on site) the error often appears in connection with a shifted neutral point / star point. This can be caused by larger consumers on the grid, for example air conditioners, pumps, large motors and lifts or by a faulty installation."
Everything I'm reading on neutral shifting indicates this is an issue with three phase sites, but we are 240 split phase. Anyone know if neutral shifting can occur on split phase services? Or is this problem only seen on three phase services?
The customer does have several heat pumps wired up without neutrals, as well as a welder that doesn't use a neutral. Also, we have another customer with the same inverters that is across the street, and they haven't had any issues with their system.