Neutral in a transfer switch

Status
Not open for further replies.

wayne123

Senior Member
Location
North Carolina
Is it OK to double up neutrals under one lug? I ask because this transfer switch that a customer bought only has three lugs for the N& G and I am feeding two sub panels out of it. The lugs are sized for two 250kcmil conductors and I put two 4/0 Al in it. There is very little space left in the TS to put any more lugs.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: Neutral in a transfer switch

Wayne,
The lugs are sized for two 250kcmil conductors
this would mean up to two 250's so the answer is yes.

As far as room in the TS, thats a different issue.

Roger
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: Neutral in a transfer switch

Hello Wayne, (neighbor) I'm in Asheville, I work for this outfit .

Roger
 

wayne123

Senior Member
Location
North Carolina
Re: Neutral in a transfer switch

Very impressive pictures. I work for Shionogi Qualicaps in Whitsett. We manufacture gelatin capsules for pharmaceutical companies.I am the plant spark chaser.
 