neutral doesn't count as current carrying ?

Status
Not open for further replies.

busman

Senior Member
Location
Northern Virginia
Occupation
Master Electrician / Electrical Engineer
Yup, as stated at the top of the list.

Here is a more complete list:

In a single phase center tap system:
1 hot + 1 neutral + 1 EGC counts as 2 CCC
2 hot + 1 neutral + 1 EGC counts as 2 CCC (presuming proper selection of hots from different legs)
2 hot + 1 EGC counts as 2 CCC
2 hot + 2 neutral + 1 EGC counts as 4 CCC (separate neutral install)

In a three phase wye system
1 hot + 1 neutral + 1 EGC counts as 2 CCC
2 hot + 1 neutral + 1 EGC counts as 3 CCC (presuming proper selection of hots from different legs)
2 hot + 0 neutral + 1 EGC counts as 2 CCC
3 hot + 1 neutral + 1 EGC counts as 3 CCC (presuming proper selection of hots from different legs)
3 hot + 0 neutral + 1 EGC counts as 3 CCC
3 hot + 2 neutral + 1 EGC counts as 5 CCC (partial separate neutral install )
3 hot + 3 neutral + 1 EGC counts as 6 CCC (presuming proper selection of hots from different legs)

In a three phase corner grounded delta system
1 hot + 1 grounded conductor + 1 EGC counts as 2 CCC
2 hot + 0 grounded conductor + 1 EGC counts as 2 CCC
2 hot + 1 grounded conductor + 1 EGC counts as 3 CCC

The three phase high leg delta system is left as an exercise for the reader :)

-Jon
Maybe I'm slow today, but it seems that 2 hots + 1 grounded on a three phase corner grounded delta system should be 3 ccc, the same as an ungrounded delta. I don't see how grounding one phase changes the currents.
 
Last edited by a moderator:

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Maybe I'm slow today, but it seems that 2 hots + 1 grounded on a three phase corner grounded delta system should be 3 ccc, the same as an ungrounded delta. I don't see how grounding one phase changes the currents.
I concur. (y)
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
Maybe I'm slow today, but it seems that 2 hots + 1 grounded on a three phase corner grounded delta system should be 3 ccc, the same as an ungrounded delta. I don't see how grounding one phase changes the currents.

You are correct. I was thinking 3 but wrote 2. I'd request that a mod edit the count since I got it wrong. *blush*

Jon
 

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
You count neutrals as current carrying when you have one hot and one neutral or two out of three 3 phase hots and a neutral. You do not count it when the neutral is part of a full MWBC and carries only the unbalanced current from the hot conductors.

The rationale is that whenever there is neutral current, one or more of the phase currents has been reduced in proportion, leaving the heat dissipation the same.
Or. Because the code says so... .
 