Maybe I'm slow today, but it seems that 2 hots + 1 grounded on a three phase corner grounded delta system should be 3 ccc, the same as an ungrounded delta. I don't see how grounding one phase changes the currents.Yup, as stated at the top of the list.
Here is a more complete list:
In a single phase center tap system:
1 hot + 1 neutral + 1 EGC counts as 2 CCC
2 hot + 1 neutral + 1 EGC counts as 2 CCC (presuming proper selection of hots from different legs)
2 hot + 1 EGC counts as 2 CCC
2 hot + 2 neutral + 1 EGC counts as 4 CCC (separate neutral install)
In a three phase wye system
1 hot + 1 neutral + 1 EGC counts as 2 CCC
2 hot + 1 neutral + 1 EGC counts as 3 CCC (presuming proper selection of hots from different legs)
2 hot + 0 neutral + 1 EGC counts as 2 CCC
3 hot + 1 neutral + 1 EGC counts as 3 CCC (presuming proper selection of hots from different legs)
3 hot + 0 neutral + 1 EGC counts as 3 CCC
3 hot + 2 neutral + 1 EGC counts as 5 CCC (partial separate neutral install )
3 hot + 3 neutral + 1 EGC counts as 6 CCC (presuming proper selection of hots from different legs)
In a three phase corner grounded delta system
1 hot + 1 grounded conductor + 1 EGC counts as 2 CCC
2 hot + 0 grounded conductor + 1 EGC counts as 2 CCC
2 hot + 1 grounded conductor + 1 EGC counts as 3 CCC
The three phase high leg delta system is left as an exercise for the reader