neutral doesn't count as current carrying ?

Status
Not open for further replies.

Stevenfyeager

Senior Member
Location
United States, Indiana
Occupation
electrical contractor
Please correct me, I thought we count neutral conductors as current carrying when we adjust for amperage when in a conduit. Table 310.15 (B) (3) (a) (Adjustment for more than 3 CCC ) But 310.15 (5) (a) says not to count them. ?? Am I wrong ? Thanks !
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
You count neutrals as current carrying when you have one hot and one neutral or two out of three 3 phase hots and a neutral. You do not count it when the neutral is part of a full MWBC and carries only the unbalanced current from the hot conductors.

The rationale is that whenever there is neutral current, one or more of the phase currents has been reduced in proportion, leaving the heat dissipation the same.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Here's a summary.

 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
A slightly different perspective: instead of asking if the _neutral_ is a CCC, instead ask 'given this set of conductors, how many CCC do I have'?

In a three phase wye system:
1 hot + 1 neutral + 1 EGC counts as 2 CCC
2 hot + 1 neutral + 1 EGC counts as 3 CCC
3 hot + 1 neutral + 1 EGC counts as 3 CCC

-Jon
 

DrSparks

The Everlasting Know-it-all!
Location
Madison, WI, USA
Occupation
Master Electrician and General Contractor
Please correct me, I thought we count neutral conductors as current carrying when we adjust for amperage when in a conduit. Table 310.15 (B) (3) (a) (Adjustment for more than 3 CCC ) But 310.15 (5) (a) says not to count them. ?? Am I wrong ? Thanks !
I always count it. You're supposed to when there are a majority of non linear loads, which is just about everything now days. LED lights, fluorescent ballasts, all electronic devices, computers. These devices all utilize switching power supplies that have harmonic currents that return to the circuit not in line with the primary phase of current. These currents have an additive effect that can overload a neutral.

Also, Google the term "super neutral," for more info on this.

Sent from my BE2028 using Tapatalk
 
I always count it. You're supposed to when there are a majority of non linear loads, which is just about everything now days. LED lights, fluorescent ballasts, all electronic devices, computers. These devices all utilize switching power supplies that have harmonic currents that return to the circuit not in line with the primary phase of current. These currents have an additive effect that can overload a neutral.

Also, Google the term "super neutral," for more info on this.

Sent from my BE2028 using Tapatalk
I think you are stuck back in the 90's. Its really not an issue now.
 

DrSparks

The Everlasting Know-it-all!
Location
Madison, WI, USA
Occupation
Master Electrician and General Contractor
I am not an expert in power electronics, but I would guess the latter. All I know is Everytime I have measured the neutral load on balanced MWBC's serving "electronic" loads, I get a value close to zero.
I know they use PF correction in data centers but not sure about LED drivers specifically. IDK, everything is always changing. I just got into the habit of running dedicated neutrals now and I'm used to it. I even get the white with colored tracers to eliminate the need for grouping.

Sent from my BE2028 using Tapatalk
 
I know they use PF correction in data centers but not sure about LED drivers specifically. IDK, everything is always changing. I just got into the habit of running dedicated neutrals now and I'm used to it. I even get the white with colored tracers to eliminate the need for grouping.

Sent from my BE2028 using Tapatalk
Although I have never seen or heard of an issue with this in modern times, I will say the NEC is rather dumb on this. They treat a load as just linear or nonlinear. Seems grossly over simplified to me as there is lots in between. In a perfect world perhaps everything would be required to have a THD value marked and there could be an accepted value where neutral currents become an issue for sizing and derating......or if modern power supplies are good enough they could just delete that stupid wording and requirement.
 

paulengr

Senior Member
NEC also has a “gotcha” clause referring to not only unbalanced currents but nonlinear currents. For instance I have clicked an 800 HP fan on a VFD with over 90 A of common mode current. It only had a ground but if it had a neutral, it would be 90 A even with balanced currents.
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
I'd like to see a motor/VFD combo that puts the common mode current the neutral.

In my experience there is no neutral circuit connection and the common mode current is via capacitive coupling to the grounded metal of the motor frame. Then this high frequency current goes everywhere in the connected grounded metal wrecking havoc with all the nearby electronics.

I guess if you built a motor with an electrostatic shield around the windings you could connect a specific circuit conductor to 'catch' this capacitive current. But even then I wouldn't want that current flowing on the neutral back to the supply transformer, I'd want to get it back to the VFD somehow.

Jon
 

clarice

Member
How many current carrying conductors do I have in 3 phase when I run 3 120 volt circuits -
A - Black
B - Red
C- Blue
and 3 neutrals ( one for each phase)?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
How many current carrying conductors do I have in 3 phase when I run 3 120 volt circuits -
A - Black
B - Red
C- Blue
and 3 neutrals ( one for each phase)?
Read through the thread and tell us how many you think there are.

Please update your profile to include your occupation and location.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Electrical Engineer - Photovoltaic Systems
A slightly different perspective: instead of asking if the _neutral_ is a CCC, instead ask 'given this set of conductors, how many CCC do I have'?

In a three phase wye system:
1 hot + 1 neutral + 1 EGC counts as 2 CCC
2 hot + 1 neutral + 1 EGC counts as 3 CCC
3 hot + 1 neutral + 1 EGC counts as 3 CCC

-Jon
For three phase systems, yes.
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
For three phase systems, yes.

Yup, as stated at the top of the list.

Here is a more complete list:

In a single phase center tap system:
1 hot + 1 neutral + 1 EGC counts as 2 CCC
2 hot + 1 neutral + 1 EGC counts as 2 CCC (presuming proper selection of hots from different legs)
2 hot + 1 EGC counts as 2 CCC
2 hot + 2 neutral + 1 EGC counts as 4 CCC (separate neutral install)

In a three phase wye system
1 hot + 1 neutral + 1 EGC counts as 2 CCC
2 hot + 1 neutral + 1 EGC counts as 3 CCC (presuming proper selection of hots from different legs)
2 hot + 0 neutral + 1 EGC counts as 2 CCC
3 hot + 1 neutral + 1 EGC counts as 3 CCC (presuming proper selection of hots from different legs)
3 hot + 0 neutral + 1 EGC counts as 3 CCC
3 hot + 2 neutral + 1 EGC counts as 5 CCC (partial separate neutral install )
3 hot + 3 neutral + 1 EGC counts as 6 CCC (presuming proper selection of hots from different legs)

In a three phase corner grounded delta system
1 hot + 1 grounded conductor + 1 EGC counts as 2 CCC
2 hot + 0 grounded conductor + 1 EGC counts as 2 CCC
2 hot + 1 grounded conductor + 1 EGC counts as 3 CCC

The three phase high leg delta system is left as an exercise for the reader :)

-Jon
 