Nema 12

Rjbushy

Electrical Contractor
Location
17356
Occupation
Owner
I am working at a Spice company requiring the use of Nema 12 enclosures. At the same time, I am being told explosion proof wiring is not necessary. Would emt and compression fittings be acceptable in these areas?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Are you talking about an area where combustible dust is the issue? If so, you never need explosion proof wiring methods for a Class II installation. Those methods are only required for flamable gas (Class I) installations. The wiring methods permitted for Class II installations are found in 502.10. 10(A) is for Division 1 locations, and 10(B) is for Division 2 locations.
 