need recommendation of nitrogen bottle and regulator to service skid transformers to re pressure nitrogen blanket. 34.5kv to550v three phase transformer, cooper material number 00022A65XXMA
 

junkhound

Senior Member
Location
Renton, WA
Occupation
EE, power electronics specialty
I know nothing about this, but do open some threads like this to see what I might learn.

Only suggestion would be to get recommendation from N2 supplier, such as Airco or whoever you would be buying the N2 from?
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
I get mine at Airgas. They have the regulators there also.less than $150 for bottle and regulator.

I buy the bottles because we keep them connected to our transformers with a regulator system that keeps the blanket at 2psi. We had a big bottle on one transformer for 25 years before it had to be replaced.

I couldn’t find that transformer with the number you provided.
I haven’t seen a padmount with an N blanket
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
could I get your email to share specifics?
Click on the persons name you want to have a private conversation with and then click "start conversation", it is not a good idea to post private email addresses in public.

Roger
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
I’m not sure exactly what’s going on with this thread but it seems my post was inappropriate for some reason but I don’t know why
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Why do transformers need an N blanket? Do all 5MVA and over have one or a bottle? Round here all the ones in my POCO's substation appear to have one.
 

grich

Senior Member
Location
MP89.5, Mason City Subdivision
Occupation
Broadcast Engineer
Why do transformers need an N blanket? Do all 5MVA and over have one or a bottle? Round here all the ones in my POCO's substation appear to have one.
In my readings of railroading, I came across an article that described in detail the Milwaukee Road's electrified lines in the Pacific Northwest. In the 1930's, I think, a substation was destroyed when lightning caused arcing in a transformer that ignited gases from the cooling oil that had built up in the open spaces above the oil. After that, the open spaces in the transformers were pressurized with nitrogen.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
In my readings of railroading, I came across an article that described in detail the Milwaukee Road's electrified lines in the Pacific Northwest. In the 1930's, I think, a substation was destroyed when lightning caused arcing in a transformer that ignited gases from the cooling oil that had built up in the open spaces above the oil. After that, the open spaces in the transformers were pressurized with nitrogen.


Is this the same phenomenon called "gassing"
 

Tony S

Senior Member
Gassing is usually caused by arcing, one of the reasons buchholz units are fitted between the tank and conservator. I’ve had two transformers fail on gas both 11/3.3kV and on each the tap changer had failed.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
That would make sense. Any idea if it can also take place from other reasons or just arcing? I know my POCO had a big issue with a few of its trafos gassing so much so they mentioned it in an annual report years back.
 

mivey

Senior Member
Why do transformers need an N blanket? Do all 5MVA and over have one or a bottle? Round here all the ones in my POCO's substation appear to have one.
Not all have a blanket. The blanket also helps keep out moisture with positive pressure. The tank breathes and when it cools it will draw in nitrogen rather than moist air. Tank seals will eventually leak.

Regular oil sample tests including DGA will help you see what is going on inside. Annual samples are highly recommended and more frequent for problem or high risk units.
 

mivey

Senior Member
That would make sense. Any idea if it can also take place from other reasons or just arcing? I know my POCO had a big issue with a few of its trafos gassing so much so they mentioned it in an annual report years back.
Overheating and chemical breakdown are key. Usually heat is the main culprit. If you have arcing in a normal transformer then you have reached a whole other level of problems.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Not all have a blanket. The blanket also helps keep out moisture with positive pressure. The tank breathes and when it cools it will draw in nitrogen rather than moist air. Tank seals will eventually leak.

Regular oil sample tests including DGA will help you see what is going on inside. Annual samples are highly recommended and more frequent for problem or high risk units.


Couldn't the air just go through a silica breather?
 
Simply need some quotes for pricing of a bottle and regulator ready to go. The project was suppose to start weeks ago, so time is crucial.
 

SceneryDriver

Senior Member
Location
NJ
Occupation
Electrical and Automation Designer
Simply need some quotes for pricing of a bottle and regulator ready to go. The project was suppose to start weeks ago, so time is crucial.

2-stage 0-15 PSI regulator from McMaster-carr:
$555.19

McMaster-Carr isn't the cheapest option, but you can have it the next day if you want. Convenience is worth something.

Call your local Praxair branch for the cost of the nitrogen bottle, size your choice. Any welding supply store should be able to sell you a N2 cylinder. Note that you want to buy it, not rent it.

I'd probably add another ~$250 for gas lines, fittings, and other associated shmoo.

This is a SWAG, based on other pneumatics projects I've done (I've never plumbed a transformer for N2).



SceneryDriver
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
Nitrogen prices: https://www.unlv.edu/sites/default/files/32/6238-PRICING.pdf

Regulator: https://www.northerntool.com/shop/t...gfqGFajVNjgsBg4jG_Ce1U2OGtlIzR3xoCS3MQAvD_BwE

get a piece of hose while your there from the regulator to the transformer gauge.

I generally either remove the gauge and insert a hose barb or go in through the previously installed bleeder.



you can get this in about an hour for less than $300 at a welding supply. They all have nitrogen, or at least did at every welding shop I’ve been to..
 
2-stage 0-15 PSI regulator from McMaster-carr:
$555.19

McMaster-Carr isn't the cheapest option, but you can have it the next day if you want. Convenience is worth something.

Call your local Praxair branch for the cost of the nitrogen bottle, size your choice. Any welding supply store should be able to sell you a N2 cylinder. Note that you want to buy it, not rent it.

I'd probably add another ~$250 for gas lines, fittings, and other associated shmoo.

This is a SWAG, based on other pneumatics projects I've done (I've never plumbed a transformer for N2).