NEC table 220.12

Status
Not open for further replies.

sharan

Senior Member
Transportation building (train station) is not listed in this table. What should be the VA/SQFT for this occupancy? Can we take energy code values for lighting to service load calculations?
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
Transportation building (train station) is not listed in this table. What should be the VA/SQFT for this occupancy? Can we take energy code values for lighting to service load calculations?

Use the connected lighting load rather than a VA/SQFT
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
Local jurisdictions may rely on architects for this information.

Since few architects are found on this forum, you might try submitting your plans to the AHJ with an RFI for train station calculations.
 
Status
Not open for further replies.
Top